1. ATTENTION returning members. If you are coming here from the old forum for the first time, you will need to reset you password. However, we had an email problem getting password reset links set out to a lot of the email addresses. That problem is temporarily rectified but IF you still have an issue, email me direct at info@thebuildingcodeforum.com and I will give you a temporary password.
    Dismiss Notice
  2. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Why is this venting not permitted?

Discussion in 'Plumbing Codes' started by Michael.L, May 15, 2019.

  1. Michael.L

    Michael.L Sawhorse

    Joined:
    May 10, 2018
    Messages:
    156
    Likes Received:
    24
    Mop Sink Drain 2.png

    I was told that my hand sink drain cannot be used to vent the mop sink because this is not part of a bathroom group. What I don't understand is, why does this not comply with Section 911 of the IPC?

    IPC 911.3 Connection at different levels.
    Where the fixture drains connect at different levels, the vent shall connect as a vertical extension of the vertical drain. The vertical drain pipe connecting the two fixture drains shall be considered to be the vent for the lower fixture drain, and shall be sized in accordance with Table 911.3. The upper fixture shall not be a water closet.​

    Could someone please explain why this plumbing does not meet code?
     
  2. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    15,676
    Likes Received:
    957
  3. jeffc

    jeffc Bronze Member

    Joined:
    Oct 23, 2009
    Messages:
    92
    Likes Received:
    11
    “Everyone does it this way.” That is just your standard vertical wet vent that has been used and legal for years. I wonder if the horizontal wet vent provisions are being inappropriately applied to this situation.
     
  4. Michael.L

    Michael.L Sawhorse

    Joined:
    May 10, 2018
    Messages:
    156
    Likes Received:
    24
    Only one floor in the building, so everything is on the same floor level. Pipe sizing is correct, as far I'm aware. I was told the issue is that the mop sink is venting through the wet discharge pipe of the hand sink. But it seems that should be acceptable according to IPC 911.3.

    I'm just trying to understand the code.
     
  5. Michael.L

    Michael.L Sawhorse

    Joined:
    May 10, 2018
    Messages:
    156
    Likes Received:
    24
    I think some confusion may come from IPC Section 912 on Wet Venting:

    912.1.1 Vertical wet vent permitted.
    Any combination of fixtures within two bathroom groups located on the same floor level is permitted to be vented by a vertical wet vent. The vertical wet vent shall be considered to be the vent for the fixtures and shall extend from the connection of the dry vent down to the lowest fixture drain connection. Each wet-vented fixture shall connect independently to the vertical wet vent. Water closet drains shall connect at the same elevation. Other fixture drains shall connect above or at the same elevation as the water closet fixture drains. The dry-vent connection to the vertical wet vent shall be an individual or common vent serving one or two fixtures.​

    Since this section addresses wet venting specifically for "within two bathroom groups" it may be that people are interpreting that (correctly or incorrectly) as excluding all wet vents for similar fixture configurations not contained within a bathroom group. But if wet venting is only permitted within bathroom groups, then how is that limitation reconciled with the Common Venting stipulated in IPC 911.3?
     
  6. Keystone

    Keystone Sawhorse

    Joined:
    Feb 23, 2010
    Messages:
    808
    Likes Received:
    104
    What Code section did the inspector cite.
     
    #6 Keystone, May 15, 2019
    Last edited: May 15, 2019
  7. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    15,676
    Likes Received:
    957


    Did the person saying it is wrong,,,

    Cite the code section that they say is in violation ????
     
  8. conarb

    conarb Sawhorse

    Joined:
    Oct 22, 2009
    Messages:
    3,391
    Likes Received:
    243
    It may be because I'm in California, which is UPC and not IPC based, but as far as I recall wet-venting has always been illegal.
     
  9. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    15,676
    Likes Received:
    957
    Is the definition the reason it is not allowed::::::


    BATHROOM GROUP. A group of fixtures consisting of a water closet, lavatory, bathtub or shower, including or excluding a bidet, an emergency floor drain or both. Such fixtures are located together on the same floor level.
     
  10. Michael.L

    Michael.L Sawhorse

    Joined:
    May 10, 2018
    Messages:
    156
    Likes Received:
    24
    This has not yet been built nor inspected. I'm planning the layout and want to ensure everything will "work" and be code compliant. I posted this configuration on a plumbing forum and was told it would not pass inspection; no codes were cited by the two plumbers who said it wouldn't pass.

    When I asked about IPC 911.3, one of the plumbers stated that he operates under UPC and that it might pass under IPC (which is the plumbing code adopted by my jurisdiction); he didn't know for sure. I'm hoping I may get a more authoritative answer on the code requirements here than on the plumbing forum.
     
  11. Michael.L

    Michael.L Sawhorse

    Joined:
    May 10, 2018
    Messages:
    156
    Likes Received:
    24
    My jurisdiction has adopted IPC, not UPC. That said, based on my reading of the 2018 UPC, wet venting is permitted. Furthermore, there is no mention of bathroom groups in the UPC section on vertical wet venting.

    UPC 908.0 Wet Venting
    908.1 Vertical Wet Venting.
    Wet venting is limited to vertical drainage piping receiving the discharge from the trap arm of one and two fixture unit fixtures that also serves as a vent not exceeding four fixtures. Wet-vented fixtures shall be within the same story; provided, further, that fixtures with a continuous vent discharging into a wet vent shall be within the same story as the wet-vented fixtures. No wet vent shall exceed 6 feet (1829 mm) in developed length.
     
  12. Michael.L

    Michael.L Sawhorse

    Joined:
    May 10, 2018
    Messages:
    156
    Likes Received:
    24
  13. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    15,676
    Likes Received:
    957
    Maybe call the locals and either email your diagram or go by and ask the question
     
  14. Michael.L

    Michael.L Sawhorse

    Joined:
    May 10, 2018
    Messages:
    156
    Likes Received:
    24
    I had previously emailed the local Building Dept official to request a preliminary meeting to discuss some issues regarding the build-out. He replied that they are too small an office to meet in advance and that I should simply submit my TI building application.
     
  15. Michael.L

    Michael.L Sawhorse

    Joined:
    May 10, 2018
    Messages:
    156
    Likes Received:
    24
    Here is the diagram from the ICC's publication on venting:

    IPC Common Venting.png
    Again, there is no discussion in IPC Section 911 that states Common Venting is restricted only to bathroom groups.
     
  16. cda

    cda Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    15,676
    Likes Received:
    957

    Submit it

    Cite the code section on the plans, so it shows you researched it and cited sections to support your design

    Do not understand why the bo can’t give you fifteen minutes

    To me it saves him time down the line

    Or maybe he is to busy to even notice the vent set up, when you submit!!!!!!
     
    my250r11, Joe Engel and Michael.L like this.
  17. HForester

    HForester Member

    Joined:
    Sep 21, 2015
    Messages:
    150
    Likes Received:
    49
    The arrangement is compliant with the IPC (and IRC) "common vent" section. Although it is not termed a "wet vent" system it is a very simple wet vent for the lower fixture.

    I don't know about the UPC...it is getting too hard to decipher that language.
     
    Michael.L likes this.
  18. Michael.L

    Michael.L Sawhorse

    Joined:
    May 10, 2018
    Messages:
    156
    Likes Received:
    24
    From my reading of the IPC (and UPC), I'm not sure how one distinguishes a "simple wet vent" from a "wet vent system." There really needs to be greater clarity in the code. Particularly in the IPC & UPC sections on Wet Venting.
     
  19. HForester

    HForester Member

    Joined:
    Sep 21, 2015
    Messages:
    150
    Likes Received:
    49
    All I am saying that is that a common vent (connecting at two different levels) is like a simple vertical wet vent...the flow from upper fixture passes through the same pipe as the venting air for the lower fixture. In your arrangement, you call it a common vent as it meets all the rules for a common vent.
     
    Michael.L likes this.
  20. Mech

    Mech Sawhorse

    Joined:
    Oct 30, 2009
    Messages:
    744
    Likes Received:
    16
    At a quick glance, you might be able to call this a waste stack vent (Section 913 in the '18 IPC) provided the pipe sizing is correct.
     