Spiral Staircase, R-3
Discussion in 'California' started by freerangequark, Sep 29, 2018.
  1. freerangequark
    freerangequark Registered User
    Sep 29, 2018
    4
    0
    I am working with a designer who said he was pretty sure that the tread width on a spiral staircase would have to be 36" wide if it is the sole means of egress from the second story of an R-3, single family home.
    REF: Referencing the 2016 California Building Code which adopts with amendments from the International Building Code 2015 (IBC 2015)
    My research has led to me to conclude that it would be permitted.
    Here is a summary of what I found. I have also provided a copy of the applicable code with pertinent items bold and/or underlined.
    1. This structure is to be an R-3 occupancy which also meets the definition of a dwelling.
    2. One means of egress is required per Section 1006.1, Exemption 1.
    3. Throughout section 1011, spiral staircases requirements fall under exceptions for construction standards.
    4. Staircase Width and Capacity Standards found in 1011.2 normally call for a 36” width, however spiral staircases are exempt from this per exemption 2 and permit a 26” width tread
    5. Section 1011.10 pertains exclusively to Spiral stairways.
    Spiral stairways are permitted to be used as a component in the means of egress only within dwelling units or from a space not more than 250 square feet (23 m2) in area and serving not more than five occupants, or from technical production areas in accordance with Section 410.6.
    A spiral stairway shall have a 71/2-inch (191 mm) minimum clear tread depth at a point 12 inches (305 mm) from the narrow edge. The risers shall be sufficient to provide a headroom of 78 inches (1981 mm) minimum, but riser height shall not be more than 91/2 inches (241 mm). The minimum stairway clear width at and below the handrail shall be 26 inches (660 mm).
    Therefore, spiral stairs are permitted as the sole means of egress in an R-3 dwelling as long as the standards specifically for spiral stairs and all other applicable sections of Chapter 10 Means of Egress are met.
    [​IMG]
    Code compliance can be achieved with a 60” diameter spiral stairway.
    A 10’ above finished floor height rise can be achieved in 11 Steps / 12 Risers.
    30 degree steps per code = 12 steps per 360 degrees = 330 degrees of rotation.
    Please let me know if I am not understanding the code correctly.
    Thank you,
    Glenn
  2. RCT
    RCT Registered User
    Dec 5, 2018
    4
    2
    Glenn,
    Pretty sure you already got your answer on this, however there is an incorrect note on your posting. Spirals have a riser restriction of 9-1/2" maximum riser which you posted.
    However, I underlined your note on the 10ft total rise with your note of 12 risers in the flight. The 10ft total rise does not comply with 12 risers, 12 risers = 10", you would need 12 steps with 13 risers to meet the 9.5" riser requirement .
    TBZ
  3. freerangequark
    Sep 29, 2018
    4
    0
    TBZ,
    Thanks for the reply... good catch!
    I actually have quotes now for two stairs which have 13 steps and 14 risers (8.6" each). They were able to get the extra step in there and maintain head clearance by using an angled deck at the top.
    Thanks,
    Glenn