1. ATTENTION returning members. If you are coming here from the old forum for the first time, you will need to reset you password. However, we had an email problem getting password reset links set out to a lot of the email addresses. That problem is temporarily rectified but IF you still have an issue, email me direct at info@thebuildingcodeforum.com and I will give you a temporary password.
    Dismiss Notice
  2. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Service Panel not quite ready?

Discussion in 'Electrical Codes' started by jar546, Feb 5, 2019.

  1. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    6,047
    Likes Received:
    316
    This is a service panel for a single family residence. The 2" conduit leaves this combo enclosure to feed a sub-panel inside the residence.

    How many violations do you see in this photo? Solely based on what you see.

    IMG_2767.jpg
     
  2. Pcinspector1

    Pcinspector1 Platinum Member

    Joined:
    Oct 28, 2009
    Messages:
    2,657
    Likes Received:
    288
    Could use some Red, White and Green tape!
     
    jar546 likes this.
  3. Rick18071

    Rick18071 Sawhorse

    Joined:
    Nov 28, 2009
    Messages:
    1,601
    Likes Received:
    142
    white or gray tape on the grounded conductor NEC 200.6
     
  4. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    6,047
    Likes Received:
    316
    Red and white, yes. Green, hmmmm not quite.
     
  5. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    6,047
    Likes Received:
    316
    There is more than marking the neutral wrong.
     
  6. LCBob

    LCBob Registered User

    Joined:
    Dec 22, 2018
    Messages:
    6
    Likes Received:
    2
    Maybe the absence of a grounding electrode conductor?
     
    jar546 likes this.
  7. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    6,047
    Likes Received:
    316
    Bingo
     
  8. LCBob

    LCBob Registered User

    Joined:
    Dec 22, 2018
    Messages:
    6
    Likes Received:
    2
    I can see the intersystem bond cover and the ground rod clamp laying in the bottom of the panel, and I can hear the electrician saying "You weren't supposed to be here 'til this afternoon."
     
  9. steveray

    steveray Sawhorse

    Joined:
    Nov 25, 2009
    Messages:
    6,070
    Likes Received:
    750
    Why is the green wire not the GEC?...Got it...missed that they were feeders....But then the GEC could be upstream somewhere that we can't see ...Like at the drip loop.....no?

    E3607.2 Location of grounding electrode conductor connection.
    The grounding electrode conductor shall be connected
    to the grounded service conductor at any accessible
    point from the load end of the overhead service conductors,
    service drop,
    underground service conductors, or service lateral
    to and including the terminal or bus to which the
    grounded service conductor is connected at the service disconnecting
    means. A grounding connection shall not be made
    to any grounded circuit conductor on the load side of the service
    disconnecting means, except as provided in Section
    E3607.3.2. [250.24(A)(1) and (A)(5)]
     
  10. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    6,047
    Likes Received:
    316
    No, no it can't. We are talking at the point of the service connection either in the meter base or service disconnect.
     
  11. ICE

    ICE Sawhorse

    Joined:
    Jun 23, 2011
    Messages:
    7,812
    Likes Received:
    728
    This cabinet appears to be intended for a bottom feed....but it’s not. Are the feed through lugs original equipment?
     
    #11 ICE, Feb 11, 2019 at 8:33 PM
    Last edited: Feb 11, 2019 at 8:46 PM
  12. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    6,047
    Likes Received:
    316
    I don't understand the question. You can see the meter section of this combo pack from above and the feeder leaving the bottom of the panel.
     
  13. ICE

    ICE Sawhorse

    Joined:
    Jun 23, 2011
    Messages:
    7,812
    Likes Received:
    728
    There’s a tunnel on the left side. And the lugs?
     
  14. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    6,047
    Likes Received:
    316
    Yes, it goes under the border fence.
     
  15. steveray

    steveray Sawhorse

    Joined:
    Nov 25, 2009
    Messages:
    6,070
    Likes Received:
    750
    Jeff...Are we talking about the same thing? 250.24(A)1 allows the GEC to attach "before the main"...Correct? As well as the section from the IRC I posted...? In which case you would not see it in the panel.....? See exhibit 250.8 in 2017 handbook...
     