1. ATTENTION returning members. If you are coming here from the old forum for the first time, you will need to reset you password. However, we had an email problem getting password reset links set out to a lot of the email addresses. That problem is temporarily rectified but IF you still have an issue, email me direct at info@thebuildingcodeforum.com and I will give you a temporary password.
    Dismiss Notice
  2. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Perpendicular door configuration

Discussion in 'Accessibility' started by rruppe20, Apr 12, 2019.

  1. rruppe20

    rruppe20 Sawhorse

    Joined:
    Mar 14, 2018
    Messages:
    5
    Likes Received:
    0
    Capture.JPG I have a customer wanting to add a door in a wall perpendicular to an existing door. The existing door swing will swing in the Maneuvering Clearance for the new door that swings into the adjacent room.
    I cannot find any regulation to prevent this design.
     
    #1 rruppe20, Apr 12, 2019
    Last edited: Apr 12, 2019
  2. JPohling

    JPohling Sawhorse

    Joined:
    Aug 16, 2011
    Messages:
    927
    Likes Received:
    74
    doors in series will need 4' between them if the swing is in the same direction, perpendicular arrangement is not illustrated
     
    rruppe20 likes this.
  3. rruppe20

    rruppe20 Sawhorse

    Joined:
    Mar 14, 2018
    Messages:
    5
    Likes Received:
    0
  4. rruppe20

    rruppe20 Sawhorse

    Joined:
    Mar 14, 2018
    Messages:
    5
    Likes Received:
    0
    Would you require 4' between he doors in the attached image? Capture.JPG
     
  5. Paul Sweet

    Paul Sweet Sawhorse

    Joined:
    Oct 17, 2009
    Messages:
    1,050
    Likes Received:
    149
    I don't think there's anything in the code to prevent this stupidity. Able and disabled people are equally inconvenienced. Nobody will get trapped (the reason for 4 ft. between doors in series) as long as there is a turning space beyond the door swings.
     
  6. JPohling

    JPohling Sawhorse

    Joined:
    Aug 16, 2011
    Messages:
    927
    Likes Received:
    74
  7. my250r11

    my250r11 Sawhorse

    Joined:
    Feb 16, 2015
    Messages:
    432
    Likes Received:
    129
    If it is a required egress door in the moe I personally would consider it an obstruction and not allow. If not, then it is not a good idea but not sure I could cite anything. Still no code for dumb yet. LOL
     
  8. JPohling

    JPohling Sawhorse

    Joined:
    Aug 16, 2011
    Messages:
    927
    Likes Received:
    74
    sure there is.............. the doors do not have clearance for accessibility around them due to the encroachment of the other door swing.
     
    my250r11 likes this.
  9. georgia plans exam

    georgia plans exam Silver Member

    Joined:
    Oct 19, 2009
    Messages:
    367
    Likes Received:
    15
    I am not aware of a code requirement that a door cannot swing into the maneuvering clearance for another door.

    GPE
     
  10. steveray

    steveray Sawhorse

    Joined:
    Nov 25, 2009
    Messages:
    6,287
    Likes Received:
    825
    I would call this maybe, but not accessibility...

    1005.7 Encroachment. Encroachments into the required
    means of egress width shall be in accordance with the provisions
    of this section.
    1005.7.1 Doors. Doors, when fully opened, shall not
    reduce the required width by more than 7 inches (178
    mm). Doors in any position shall not reduce the required
    width by more than one-half.
     
    my250r11 likes this.
  11. JPohling

    JPohling Sawhorse

    Joined:
    Aug 16, 2011
    Messages:
    927
    Likes Received:
    74
    it would be dependent upon if this is an accessible route where the doors are used in series.
    CBC 11B-404.2.6 Doors in series or gates in series: The distance between two hinged or pivoted doors in series and gates in series shall be 48 inches minimum plus the width of doors or gates swinging into the space.
     
  12. steveray

    steveray Sawhorse

    Joined:
    Nov 25, 2009
    Messages:
    6,287
    Likes Received:
    825
    As long as there is maneuvering past the door swing, it is not an issue.....

    Typically, the doors-in-series condition occurs in entry
    vestibules that are used to reduce the infiltration of outside
    air. It is important to realize that this requirement applies
    only when the user must pass through two doors in succession.
    The requirement would not be applicable if, instead
    of a vestibule, the situation was a corridor and the two
    doors were into offices located on opposite sides of the
    corridor. A storm or screen door immediately in front of an
    entrance door or communicating doors between two hotel
    rooms are not considered doors in a series.
    Swinging doors in series when placed too closely
    together can create a condition where a person using a
    wheelchair may pass through one door, and still have to
    hold that door open while trying to open the second door.
    To resolve this condition, a minimum distance of 48 inches
    (1220 mm) is required between the doors if the doors
    swing away from each other or 48 inches (1220 mm) plus
    the width of any door swinging into the space is required
    [see Figure 404.2.5 and Commentary Figure C404.2.5(a)].
    Doors in a series are not always in a straight line. Doors
    may be offset, or located on adjacent walls rather than
    opposite walls. The intent is that a clear floor space for a
    wheelchair [i.e., 30 inches by 48 inches (765 by 1220
    mm)] is available past the swing of the first door so the
    person entering can let one door close before they start to
    open the second door [see Commentary Figure C404.2.5
    (b)].
     
    my250r11 likes this.