1. ATTENTION returning members. If you are coming here from the old forum for the first time, you will need to reset you password. However, we had an email problem getting password reset links set out to a lot of the email addresses. That problem is temporarily rectified but IF you still have an issue, email me direct at info@thebuildingcodeforum.com and I will give you a temporary password.
    Dismiss Notice
  2. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Exhaust Flue Piping

Discussion in 'Fuel Gas Codes' started by north star, Apr 10, 2019.

  1. north star

    north star Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    3,671
    Likes Received:
    226
    $ = $ = $ = $

    I have some existing, natural gas, Forced Air [ Heating ] Units
    that are being replaced with Infrared heaters........The FAU's

    have exhaust flues that penetrate the roofing assembly.

    A Contractor is proposing to remove the FAU's & install rain caps
    on the exhaust pipes, and leave it like that.

    QUESTION: Is there a Code section that "requires" the exhaust

    piping to be removed when the appliances themselves are
    removed ?..........We are using the `15 IFGC & the other `15
    I-Codes.

    Thanks ya`ll ! :cool:


    $ = $ = $ = $
     
  2. steveray

    steveray Sawhorse

    Joined:
    Nov 25, 2009
    Messages:
    6,287
    Likes Received:
    825
    Energy code for building envelope would be where I would look...

    C402.5 Air leakage—thermal envelope (Mandatory). The
    thermal envelope of buildings shall comply with Sections
    C402.5.1 through C402.5.8, or the building thermal envelope
    shall be tested in accordance with ASTM E 779 at a pressure
    differential of 0.3 inch water gauge (75 Pa) or an equivalent
    method approved by the code official and deemed to comply
    with the provisions of this section when the tested air leakage
    rate of the building thermal envelope is not greater than 0.40
    cfm/ft2 (0.2 L/s · m2). Where compliance is based on such
    testing, the building shall also comply with Sections
    C402.5.5, C402.5.6 and C402.5.7.
    C402.5.1 Air barriers. A continuous air barrier shall be
    provided throughout the building thermal envelope. The
    air barriers shall be permitted to be located on the inside or
    outside of the building envelope, located within the assemblies
    composing the envelope, or any combination thereof.
    The air barrier shall comply with Sections C402.5.1.1 and
    C402.5.1.2.
     
    north star likes this.
  3. north star

    north star Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    3,671
    Likes Received:
    226
    & 0 & 0 &

    Thank you **steveray** ! ;)

    & 0 & 0 &
     
  4. steveray

    steveray Sawhorse

    Joined:
    Nov 25, 2009
    Messages:
    6,287
    Likes Received:
    825
    If they "sealed it and stuffed it with insul, I would not be concerned....Maybe put a note on it on the roof side that says remove when reroofing?
     
  5. Keystone

    Keystone Sawhorse

    Joined:
    Feb 23, 2010
    Messages:
    804
    Likes Received:
    103
    I would take issue with the exhaust flue piping remaining in place, cite IFGC 305.1. “equipment and appliances shall be installed as required by the terms of their approval, in accordance with the conditions of listing....”

    The flue is no longer serving an appliance as approved & intended, placing a cap or any other material not approved by the listing authority is a violation.
     
  6. north star

    north star Sawhorse

    Joined:
    Oct 19, 2009
    Messages:
    3,671
    Likes Received:
    226
    @ : @ : @

    Thank you for the information **Keystone** ! ;)

    @ : @ : @
     
  7. Paul Sweet

    Paul Sweet Sawhorse

    Joined:
    Oct 17, 2009
    Messages:
    1,050
    Likes Received:
    149
    They should be removed so somebody in the future can't hook up an appliance without noticing that the vent is capped and suffocating everybody in the building.
     
  8. Flexo

    Flexo Registered User

    Joined:
    Jan 28, 2018
    Messages:
    29
    Likes Received:
    3
    This reminds me of an incident I had about 20 years ago. I reroofed a home and with the owners consent, removed the protruding portion of a dilapidated, unlined brick chimney that was a vestige from when kitchens had wood fired cookstoves. Later the owner informed me that the gas company would not turn the gas on due to the water heater being vented into the now roofed over chimney.
     