1. ATTENTION returning members. If you are coming here from the old forum for the first time, you will need to reset you password. However, we had an email problem getting password reset links set out to a lot of the email addresses. That problem is temporarily rectified but IF you still have an issue, email me direct at info@thebuildingcodeforum.com and I will give you a temporary password.
    Dismiss Notice
  2. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

electric tankless water heater UL 499

Discussion in 'Plumbing Codes' started by Flexo, Jul 10, 2018.

  1. Flexo

    Flexo Registered User

    Joined:
    Jan 28, 2018
    Messages:
    26
    Likes Received:
    3
    Are you or your jurisdiction requiring P&T valves on electric tankless water heaters? We use the 2012 codes,
    P2803.1 in the IRC requires all residential water heaters to have P&T relief valves. UL 499 allows for no P&T relief for electric tankless units meeting the UL 499 standard. I know that the IRC would preempt the UL and that the most restrictive regulation shall govern. Does your jurisdiction require a P&T relief valve in this instance?
    Thank you.
     
  2. Pcinspector1

    Pcinspector1 Platinum Member

    Joined:
    Oct 28, 2009
    Messages:
    2,742
    Likes Received:
    325
    The ones I've inspected so far have been installed, did not know that there was a UL 499 exemption.
     
    Francis Vineyard likes this.
  3. ICE

    ICE Sawhorse

    Joined:
    Jun 23, 2011
    Messages:
    7,901
    Likes Received:
    774
    I've never inspected one. It may come down to the volume that the heater can contain. For example, pool heaters are seldom equipped with a TPR valve but the volume of the coil qualifies the heater as a storage capacity heater and as such requires a TPR valve.

    Gas fired tankless water heaters always have one. A reasonable assumption is that the coil holds enough water to be classified as a storage capacity water heater.
     
  4. Rick18071

    Rick18071 Sawhorse

    Joined:
    Nov 28, 2009
    Messages:
    1,658
    Likes Received:
    157
    I saw a few the said right on the unit that a P&T is required, that is the only time I required it.
     
  5. Francis Vineyard

    Francis Vineyard Sawhorse

    Joined:
    Jan 1, 2010
    Messages:
    3,113
    Likes Received:
    415
    Don't recall all the complexities of how the fuel-fired tankless system works but my understanding is the fuel burns at one temperature and therefore has the potential to exceed the temperature for the flow of water to be heated and require a PTR valve. Whereas electric has a duty cycle (on/off) and better control the heat the water to the set temperature.

    An example of a manufacturer's installation guideline of an whole house electric tankless unit invites

    NOTICE.JPG

    A code change proposal:
    RP54-13 P2803.1, P2803.2 (New)
    Revise as follows:
    P2803.1 Relief valves required.
    Storage water heaters and hot water storage tanks shall be protected against over-pressure and over-temperature conditions by one of the following methods:

    1. A separate pressure-relief valve and a separate temperature-relief valve

    2. A combination pressure- and temperature-relief valve.

    P2803.2 Instantaneous fuel-gas fired water heater relief valve.
    A fuel-gas fired instantaneous water heater shall be protected against over-pressure conditions by a pressure relief valve. The valve shall be located on the cold water inlet piping to the heater at a point that is downstream of all external valves except where the heater manufacturer’s instructions require the valve be located elsewhere.

    Committee Action: Disapproved Committee Reason: This proposal doesn’t address small tankless water heaters. The manufacturer’s instructions take precedence. https://www.iccsafe.org/wp-content/uploads/10-IRC-P.pdf

    R102.4 Referenced codes and Standards.
    The codes and standards reference in the code shall be considered part of the requirements of this code to prescribed extent of each such reference and as further regulated in Section R102.4 and R102.4.2

    Exception : where enforcement of a code provision would violate the conditions of the listing of the equipment or appliance, the conditions of the listing and manufacturer’s instructions shall apply.

    R102.4.1 Conflicts. Where conflicts occur between provisions of this code and referenced codes and standards, the provisions of the code shall apply.

    R102.4.2 Provisions in referenced codes and standards.
    Where the extent of the reference to a referenced code or standard includes subject matter that is within the scope of this code, the provisions of this code, as applicable, shall take precedence of the provisions in the reference code or standard.
     
    #5 Francis Vineyard, Jul 10, 2018
    Last edited: Jul 10, 2018
    ICE and Pcinspector1 like this.
  6. HForester

    HForester Member

    Joined:
    Sep 21, 2015
    Messages:
    137
    Likes Received:
    44
    The proposal's reason statement:

    "A question that is often asked is whether existing Section P2803.1 applied to instantaneous (“tankless”) water heaters as it is impossible to install a temperature relief valve (in accordance with Section P2803.4) as there is no tank! A new section is added to cover gas instantaneous (“tankless”) water heaters. The fuel gas-fired instantaneous water heater industry is waffling about whether a pressure relief valve is required and most have in their instructions “ it’s up the local code official or jurisdiction”. Many questions come up about this and code officials are not sure what to do. We need to settle the debate by simply requiring the pressure relief valve at least for the gas-fired tankless water heaters. Note that electric instantaneous water heaters are exempt from having a PRV by the UL listing for those products. While the code could be written to require PRVs for electric tankless water heaters, it is impractical to install PRVs for the small electric units (think of the one fixture, under the cabinet type) and then the issue is where to route the discharge pipe. Generally, the gas instantaneous (“tankless”) water heaters are for the whole building and are installed in a basement, garage or other location (outside) where routing of the PRV pipe is no more difficult than it is for a storage tank water heater."

    It seems to me that if UL doesn't care about a pressure relief valve for electric tankless water heaters (of any size) why should the code be worried? An overabundance of caution will only lead to complications (where to route the discharge?) that will virtually eliminate anyone choosing to use small [electric] tankless units.
     
  7. sharoncynthia

    sharoncynthia Registered User

    Joined:
    Feb 5, 2019
    Messages:
    1
    Likes Received:
    0
    Before hiring any water heater installation expert ask referrals and then askthem about their work. Company with poritive feedback must be chosen for your heater repair.
     
    #7 sharoncynthia, Feb 5, 2019
    Last edited by a moderator: Feb 5, 2019
  8. steveray

    steveray Sawhorse

    Joined:
    Nov 25, 2009
    Messages:
    6,163
    Likes Received:
    771
    Required....as long as it does not void the listing....

    P2609.2 Installation of materials. Materials used shall be
    installed in strict accordance with the standards under which
    the materials are accepted and approved. In the absence of
    such installation procedures, the manufacturer’s instructions
    shall be followed. Where the requirements of referenced standards
    or manufacturer’s instructions do not conform to the
    minimum provisions of this code, the provisions of this code
    shall apply.
     
  9. HForester

    HForester Member

    Joined:
    Sep 21, 2015
    Messages:
    137
    Likes Received:
    44
    It doesn't make sense to try to install a temperature relief valve on any tankless unit because it can't be installed in accordance with the listing: The probe must be located withing the top 6 inches of the storage tank.
     
  10. steveray

    steveray Sawhorse

    Joined:
    Nov 25, 2009
    Messages:
    6,163
    Likes Received:
    771
    Deleted......
     
  11. leonoro

    leonoro Registered User

    Joined:
    Mar 9, 2019
    Messages:
    2
    Likes Received:
    0
    I want more ideas. Anyone help me ?
     
  12. Flexo

    Flexo Registered User

    Joined:
    Jan 28, 2018
    Messages:
    26
    Likes Received:
    3
    Thanks for all of your answers. The gas fired instant water heaters that I have inspected have all had provision for P&T valves. In several instances where there the P&T was missing, upon re-inspection it was installed. My question was generated due to an electric instant water heaters that had no provision for a pressure and temperature relief valve, this surprised me, so I learned more regarding UL 499. I certainly respect all of the collective knowledge here, so I thought that I would inquire how you handle this conflict between the code requirement and the UL listing.
    Leonoro, what do you need to know. Be specific.
     
  13. jar546

    jar546 *****istrator

    Joined:
    Oct 16, 2009
    Messages:
    6,224
    Likes Received:
    369
    I am glad that this has been resurrected. I see a lot of these installed in high rise condo's but I am not inspecting the plumbing end anymore.
     
  14. leonoro

    leonoro Registered User

    Joined:
    Mar 9, 2019
    Messages:
    2
    Likes Received:
    0
    :)
     
  15. Builder Bob

    Builder Bob Sawhorse

    Joined:
    Oct 17, 2009
    Messages:
    2,034
    Likes Received:
    266
    Might be time to ask ICC for a formal interpretation..... what a quandary
     
  16. MikeC

    MikeC Silver Member

    Joined:
    May 17, 2012
    Messages:
    222
    Likes Received:
    3
    IPC 504.4 specifies "storage water heaters" when requiring a relief valve. Tankless water heaters are not storage water heaters.

    IRC P2803.1 requires a relief valve on appliances used for heating water or store hot water - so this required here, except maybe by R102.4 in the exception where it states the conditions of the listing shall apply if the code would violate the listing. So list leads to the question of - would an inline relief valve violate the listing? I doubt it would. Now, as it has already been stated, while a pressure relief valve may be installed inline near the appliance, the temperature relief valve is required to be installed in the tank which is impossible due to the lack of a tank. This brings up the question of - if one is required by code and it shall be installed in the storage tank, can you require the installation of a storage tank when there is a water heater present? I would never do this, but the code does lead you in that direction.

    So, my take on this is:
    Structures built under the IRC require a relief valve for all water heaters & hot water storage tanks. If there is no provision for a temperature relief valve on the appliance and no instructions on how to install one, only a pressure relief valve is required.
    All other structures only require a relief valve when there is storage of hot water.
    This wording has followed through into the 2018 I-codes
     
    jar546 and Rick18071 like this.
  17. MikeC

    MikeC Silver Member

    Joined:
    May 17, 2012
    Messages:
    222
    Likes Received:
    3
    Okay, I feel the need to add one thing to my post above. IF the appliance is not a listed appliance - the code is enforced 100%. There is way too much crap for sale on ebay & amazon that doesn't meet any standard and, IMHO, shouldn't be installed anywhere.
     