    We are adding a mezzanine to a library, which is part of a one story school building. The school really wants to glaze the mezzanine wall (rather than having just a railing overlooking the library), so in order to do this, we have to add another means of egress to the mezzanine, which will take the form of an exterior staircase down to the deck outside the library. Does this egress stair have to be covered? See attached image for reference. Thanks!
  2. cda
    cda Sawhorse
    Oct 19, 2009
    15,611
    950
    Welcome!!!!
  3. cda
    cda Sawhorse
    Oct 19, 2009
    15,611
    950
    Well no attached , maybe because you are new or not a paying sawhorse
    Anyway, what building code and edition???
    I am thinking not required, just not sure how you get away with weather problems on the tread ?
    Just wait for more posts
  4. Kendra
    Aug 25, 2017
    7
    0
    Sorry! I can figure out how to attach an image :(
  5. cda
    cda Sawhorse
    Oct 19, 2009
    15,611
    950
    Some convert it to a link and post.
    Sometimes that works
  6. cda
    cda Sawhorse
    Oct 19, 2009
    15,611
    950
    1003.4 Floor surface.
    Walking surfaces of the means of egressshall have a slip-resistant surface and be securely attached.
    1011.7.2 Outdoor conditions.
    Outdoor stairways and outdoor approaches to stairways shall be designed so that water will not accumulate on walking surfaces.
  7. Francis Vineyard
    Francis Vineyard Sawhorse
    Jan 1, 2010
    3,113
    415
    It does not have to be covered and if it is adequate ventilation opening should be addressed.
    2015 IBC (2012 is section 1026)
    1027.3 Open side. Exterior exit stairways and ramps serving as an element of a required means of egress shall be open on not less than one side, except for required structural columns, beams, handrails and guards. An open side shall have not less than 35 square feet of aggregate open area adjacent to each floor level and the level of each intermediate landing. The required open area shall be located not less than 42 inches above the adjacent floor or landing level.
    1027.4 Side yards. The open areas adjoining exterior exit stairways or ramps shall be either yards, courts or public ways; the remaining sides are permitted to be enclosed by the exterior walls of the building.
    1027.5 Location. Exterior exit stairways and ramps shall have a minimum fire separation distance of 10 feet measured at right angles from the exterior edge of the stairway or ramps, including landings, to:
    1. Adjacent lot lines.
    2. Other portions of the building.
    3. Other buildings on the same lot unless the adjacent building exterior walls and openings are protected in accordance with Section 705 based on fire separation distance.