    Dismiss Notice
    Dismiss Notice
ADA Compliant Locks for Swimming Pool Gates? And Exit access
Discussion in 'Door & Hardware forum *Sponsored by Allegion' started by tbz, Apr 12, 2019.
  1. tbz
    tbz Silver Member
    Sep 10, 2010
    484
    13
    Designing (3) gates for around a resident swimming pool in a student housing location. Pool sits between 2 buildings. The barriers are being installed for separation, the question comes to the locks for the gates.
    The need to meet ADA, I would prefer not to install regular every day lever locks. The unit I am looking at says it is ADA compliant, but is a push button activated lock complaint with ADA & is it also allowed for MOE egress on the gates for exiting?
    This is the lock I am thinking of using I will also put the weblink after the video.
    Weblink to the product: Being this is outside I was trying to keep it relatively non metallic.
    As to the installation, the pool needs to be locked when closed, but the interior still needs to be able to exit. Also, my understanding is the lock can not be up at 54" because of ADA, thus the entire area needs to have screen protection from all angles with mesh less than 1/2" in openings within 18" of the edges of the lock, is this correct?
  2. ADAguy
    ADAguy Sawhorse
    Sep 11, 2013
    3,098
    279
    What is the basis for their contention of ADA compliant?
  3. steveray
    steveray Sawhorse
    Nov 25, 2009
    6,346
    833
    We typically see a panic on the inside per OL....
  4. LGreene
    LGreene Sawhorse
    Staff Member
    Oct 20, 2009
    1,097
    84
    This seems more like a residential product. If the occupant load of the pool area is 50+, you will probably need panic hardware. Von Duprin has a pool modification for the 99 series, which puts the panic at code-compliant height, and the outside trim at 54 inches.
  5. tbz
    tbz Silver Member
    Sep 10, 2010
    484
    13
    Thank you Just the direction I was looking for, I was not able to find the trim for the 54" height release on their website, do you happen to know the part number?
  6. steveray
    steveray Sawhorse
    Nov 25, 2009
    6,346
    833
    7. Access doors or gates in barrier walls and fences
    protecting pools, spas and hot tubs shall be permitted
    to comply with Section 1010.1.9.2.
    1010.1.9.2
    Exception: Access doors or gates in barrier walls
    and fences protecting pools, spas and hot tubs shall
    be permitted to have operable parts of the release of
    latch on self-latching devices at 54 inches (1370
    mm) maximum above the finished floor or ground,
    provided the self-latching devices are not also self-
    locking devices operated by means of a key, electronic
    opener or integral combination lock.
    #6 steveray, Apr 15, 2019
  7. Rick18071
    Rick18071 Sawhorse
    Nov 28, 2009
    1,806
    186
    What code and section is the above #7 in?
  8. steveray
    steveray Sawhorse
    Nov 25, 2009
    6,346
    833
  9. Rick18071
    Rick18071 Sawhorse
    Nov 28, 2009
    1,806
    186
    Odd this section (above) is under doors but not under the gate section. I still can't find where section #7 is at. Don't know why this would be in the 2015 IBC at all because the 2015 IBC requires pools to comply by the International Pool and Spa Code. I can't find the same exception in there but only says what to do if under 54" which would not be accessible:
    ISPSC 305.3.3 Latches. Where the release mechanism of the
    self-latching device is located less than 54 inches (1372
    mm) from grade, the release mechanism shall be located
    on the pool or spa side of the gate not less than 3 inches
    (76 mm) below the top of the gate, and the gate and barrier
    shall not have openings greater than 1/2 inch (12.7 mm)
    within 18 inches (457 mm) of the release mechanism.
    In ANSI 117.1 - 2006 there nothing about gates or anything about this under door hardware. Section 1110.4.13 Swimming Pools, wading pools, hot tubs and spas also does not mention gates but does require swimming pools to be accessible.
    I don't enforce ADA so I am only trying to make sence of the ICC codes.
  10. steveray
    steveray Sawhorse
    Nov 25, 2009
    6,346
    833
    My bad Rick...Ch 11 2015 IBC
    1109.13 Controls, operating mechanisms and hardware.
    Controls, operating mechanisms and hardware intended for
    operation by the occupant, including switches that control
    lighting and ventilation and electrical convenience outlets, in
    accessible spaces, along accessible routes or as parts of
    accessible elements shall be accessible.
    1. Operable parts that are intended for use only by service
    or maintenance personnel shall not be required
    to be accessible.
    2. Electrical or communication receptacles serving a
    dedicated use shall not be required to be accessible.
    3. Where two or more outlets are provided in a kitchen
    above a length of counter top that is uninterrupted
    by a sink or appliance, one outlet shall not be
    4. Floor electrical receptacles shall not be required to
    be accessible.
    5. HVAC diffusers shall not be required to be accessible.
    6. Except for light switches, where redundant controls
    are provided for a single element, one control in
    each space shall not be required to be accessible.
  11. LGreene
    LGreene Sawhorse
    Staff Member
    Oct 20, 2009
    1,097
    84
  12. Rick18071
    Rick18071 Sawhorse
    Nov 28, 2009
    1,806
    186
    While we are on the subject do accessible gates need to have the same rules as doors? ANSI 117.1 doesn't say anything about gates except for one section while the IBC does have a section on gates.
    1. Clear width
    2. Maneuvering clearances.
    3. Door Hardware (no tight gasping, pinching, or twisting of wrist)
    4. Closing speed
    5. Door-opening force
    6. Door surface (smooth surface 10" from floor)
    The only thing I can find about gates is:
    404.2.1 Double-Leaf Doors and Gates.
    Interested in what ADAGUY has to say too.
  13. LGreene
    LGreene Sawhorse
    Staff Member
    Oct 20, 2009
    1,097
    84
    The 2017 edition of A117.1 has been updated to include the word "gates" in the door-related sections. This edition has not yet been referenced by the IBC, but the 2009 edition says: "404.2 Manual Doors. Manual doors and doorways, and
    manual gates, including ticket gates, shall comply with Section 404.2." The 2010 ADA standards specifically reference gates in the individual sections. I believe the intent is for gates on an accessible route to be subject to the same requirements as doors on an accessible route.
  14. ADAguy
    ADAguy Sawhorse
    Sep 11, 2013
    3,098
    279
    Response:
    The ongoing disconnect and enforcement of the ADA continues to be a "legal" issue. Federal government created a minimum standard with the belief that states would issues enforcement mechanisms with which to make it local law to comply. They chose to make those with disabilities to be the "cops" so to speak but lack the resources to follow up on all but the largest instances of noncompliance.
    If state AG's had accepted and enacted a responsibility to require upgrading local codes/ code enforcement to handle enforcement locally (much as Massachusetts did in 1967 (prior to the ADA)) and not relied upon the A117.1 we wouldn't be continuing to point the finger at code.
    Consider that if barriers still exist in facilities constructed new or remodeled since the ADA, that were required to be compliant, is it not then the duty of local code enforcement to respond to complaints for noncompliance with code? and if local codes using A117.1 are less than the minimums of ADASAD, is not the States AG's then not in compliance with federal law?
  15. Rick18071
    Rick18071 Sawhorse
    Nov 28, 2009
    1,806
    186
    My duty as an building code officer is to follow the law of the state. In PA we have a Uniiform Construiton Code. It diesn't say anything about ADA, ADASAD or responding to any complaints at all about anything.
  16. Paul Sweet
    Paul Sweet Sawhorse
    Oct 17, 2009
    1,062
    153
    ADASAD and ANSI 117.1 are probably 98% the same. ADAAG and ADASAD were both based on the ANSI A117.1. The feds just made a few modifications and additions. Most of them have been incorporated elsewhere in the IBC or updated ANSI A117.1. ADAAG & ADASAD contain some operating provisions which are outside the scope of a building code. Actually, ANSI A117.1 goes beyond ADASAD in a few instances, such as vertical grab bars and larger turning circles.
  17. ADAguy
    ADAguy Sawhorse
    Sep 11, 2013
    3,098
    279
    ANSI is "free to exceed" but not be "less than" ADASAD, therein lies the cunumdrum in many states.
  18. Builder Bob
    Builder Bob Sawhorse
    Oct 17, 2009
    2,057
    272
    Although we do not enforce ADA, great strides have been made to make sure ADA and ANSI A117.1 are more compatible, however, ADA is still the responsibility of the contractor, designer, and developer - and decisions concerning accessibility (such as should the second floor of a fire house be accessible) can be supported by searching DOJ website for interpretations - The answer by the way, is it is required for a second story of a fire house to be accessible- letter of interpretation from DOJ/ ADA dated February,19,1999
    ADAguy and my250r11 like this.
  19. ADAguy
    ADAguy Sawhorse
    Sep 11, 2013
    3,098
    279
    Thank you for this Bob.
    Builder Bob likes this.
Share This Page