    Dismiss Notice
    Dismiss Notice
1HR INTERIOR WALL
Discussion in 'Website Discussion' started by Alejandro Bustamante, Dec 13, 2018.
  1. Alejandro Bustamante
    Alejandro Bustamante Registered User
    Dec 8, 2018
    4
    0
    Does an interior 1 hr fire rated non-bearing wall need type X Gyp. Bd. on both sides?
    Thank you.
  2. mtlogcabin
    mtlogcabin Sawhorse
    Oct 17, 2009
    6,924
    650
    Normally yes however it will depend on the assembly you choose
    There are assemblies that do not include studs GA WP 1311 and 1330
  3. Alejandro Bustamante
    Dec 8, 2018
    4
    0
    So the wall between the Garage and the livable space in a residence has to have Gyp. Bd. Type X on both sides?
  4. mtlogcabin
    mtlogcabin Sawhorse
    Oct 17, 2009
    6,924
    650
    It only has to be half inch regular drywall not type X
  5. ICE
    ICE Sawhorse
    7,756
    707
    Is there living space above the garage? Is this a single family dwelling?
  6. Ty J.
    Ty J. Sawhorse
    Aug 2, 2017
    219
    103
    We need more information to answer your questions...
    Is this a single family dwelling? What code is enforced in your area? Is this new construction or existing?
  7. rktect 1
    rktect 1 Gold Member
    Oct 20, 2009
    808
    15
    You need a rated assembly. If it specifies type X, then that is what you use.
  8. rktect 1
    Oct 20, 2009
    808
    15
    Does your city require a one hour rated wall between the garage and living space? The village I work in only requires 5/8" type X on the garage side, not a 1 hr rated wall.
  9. Alejandro Bustamante
    Dec 8, 2018
    4
    0
    You mean the the gyp. bd facing the livable space. Right?
    ICE, yes there is a livable space above the garage.
  10. mtlogcabin
    mtlogcabin Sawhorse
    Oct 17, 2009
    6,924
    650
    Below is what the IRC requires CA is a different animal and maybe more restrictive
    R302.6 Dwelling/garage fire separation.
    The garage shall be separated as required by Table R302.6. Openings in garage walls shall comply with Section R302.5. This provision does not apply to garage walls that are perpendicular to the adjacent dwelling unit wall.
    TABLE R302.6
    DWELLING/GARAGE SEPARATION
    SEPARATION MATERIAL
    From the residence and attics Not less than 1/2-inch gypsum board or equivalent applied to the garage side
    From all habitable rooms above the garage Not less than 5/8-inch Type X gypsum board or equivalent
    Structure(s) supporting floor/ceiling assemblies used for separation required by this section Not less than 1/2-inch gypsum board or equivalent
  11. Alejandro Bustamante
    Dec 8, 2018
    4
    0
    Thanks to all. Your answers helped me!!!
  12. mark handler
    mark handler Sawhorse
    Oct 25, 2009
    9,804
    589
    Depends on the jurisdiction; some have Up'ed to 5/8" some allow the 1/2 inch.
Share This Page